JFletcher
- Williamsburg, VA
I will be installing the following:
~ One gfci receptacle in a half bath, one in the full bath
~ 4 keyless lights on 3-way switches in the attic, one receptacle
~ 6 keyless lights in the crawlspace, one receptacle for a pipe heat trace, one for general use
I plan to pull a 12/3 (20A mwb circuit) to the half bathroom gfci then a 12/2 from that to the full bath gfci, and run a 14/3 (15a mwbc) for the attic receptacle/lights, then a 14/2 from the attic to the crawlspace.
I know the crawlspace receptacle needs to be GFCI protected; do any of the lights or attic receptacle need it as well? The receptacles are general use and not for any equipment. Is a zip-tie an acceptable way of grouping the conductors of the MWBCs in the panel? Would a 2p breaker be better/worse than two 1p breakers with handle ties? Also, can I use 15A duplex GFCI receptacles in the bathrooms or do they have to be 20A? Lastly, do the crawlspace receptacles need to be WR?
VA residential is under the 2012 IRC