mbrooke
Batteries Included
- United States
- Technician
What is the typical cost of a new 345 or 115kv 63ka dead tank breaker?
Nothing "typical" about those, huge variance
Most are live tank now.
:lol::lol:
But that does certainly explain a lot![]()
I've seen that around the world, but not so much in the US. We use dead tank 90% of the time for both existing and new installations (see pic). But since you bring it up, why is live tank preferred over dead tank? What advantages do live tank breakers have?
What factors play in the cost?
What medium are they using for the arc quenching?
SF6 is unpopular due to environmental issues, so air blast became the norm. That said there were complaints about noise with the early units.
OEM, design, ratings, features, locations, etc... but figure somewhere in the $250-$350k range if you are just curious. And they still typically use SF6, just less gas than older styles.
I represent that insinuation
live tanks are cheaper, about the only reason I can see
although they require external CT's which offset some of the savings
SF6, still common in the US if I am correct. My understanding is that vacuum only works at lower voltages.
How much does interrupting capability add to the breaker, ie 20ka, 40ka 63ka? Also what do you mean by OEM (custom)?
I have it on good authority that you are somewhere around $95K for the 115KV and $270K for the 345kV. And as an added bonus even though you didn't ask, $150K for 230KV.
These are for 63kA.
ten years ago, SF6 was what all the new stuff being installed around where i was at was using.... but the
environmental issues were rearing their ugly head at that time, to the extent that LADWP had bought some
enormous amount of SF6, to cover their needs for 50 or 60 years of maintenance on all their SF6 gear....
i don't know if there is any agent that could be substituted for SF6, and i'm thinking opening or closing a
SF6 switch that wasn't fully charged, would not be a good experience.