If you are suppose to shunt trip any 125v devices underneath an exhaust hood, and all 125v, 15-20 amp devices in the same kitchen shall be protected by ground fault devices (breakers or receptacles), Then what do you do when you have a device that falls under both of those rules and requires shunt tripping because of being underneath the hood, but in the other hand, also requires ground fault protection. I don't want to install a GFCI receptacle behind the equipment. The only option I can think of is install a subpanel near the hood and shunt trip the sub panel. Is there any other option? Thanks!