electricblue
- Largo, Florida
- EC
Any ideas on a better conduit to use than rmc under a saltwater dock? Ocal came to mind but I don't trust the cut joints? I was asked by owner if they make ss conduit.
RTRC-XW [Article 355; Section 355.10(F); Section 501.10(B)(1)(6)] is acceptable in Division 2. Be careful it carries the "XW" suffix. It is practically, the standard for under-dock installations at the Port of Long Beach.
Also be careful to observe the grounding/bonding requirements of Section 501.30. I recommend avoiding any intermediate RMC in a run; it doesn't bond well.
That product would be fine. Sorry your general didn't win.
Under a dock, GRC type RMC doesn't stand a chance with typical marine debris.
In the future, in addition to the cautions I mentioned earlier, you would do well to have a qualified structural engineer design the support system. Also be aware that, installed properly, the system can be close to air-tight and it will "float" under the right conditions - another reason for a qualified structural support design.
Also see the second sentence of Section 355.30(B) for an interesting installation application. With supporting qualified (Structrual PE) calculations, UL can be pretty generous with support spacing.