[FONT=verdana, geneva, lucida, lucida grande, arial, helvetica, sans-serif]Hi, I'm a new member and this is my first post. I have posted this same question in 3 other forums and only received a related reply in one, as well as a private message from someone there to try the Mike Holt forum. I am not shopping for an answer that suits me, just an answer to the question.[/FONT]
The company I work for does service work at retail gas stations, specifically the pump and tank work. We have two electricians on staff for service/small job work. No real heavy electrical work, when we build a new station we sub out the electric. One of the tasks our electricians perform on a routine basis is to replace the gas dispensers with new models. The challenge we come up against quite frequently at older stations is there is only on conduit to the gas dispenser. A modern gas dispenser needs three circuit types, a Class 1 for the power, a Class 2 or 3 for the intercom, and a communications circuit in the form of Cat. 5 cable rated for a hazardous location. My question has to do with combining all three circuit types into that one conduit. I think it can be done per code, but can someone confirm? Here is why I think it can be done:
[FONT=verdana, geneva, lucida, lucida grande, arial, helvetica, sans-serif]The Class 2/3 circuit can be reclassified and combined in a raceway with a Class 1 circuit per Sec. 725.130 as long as you remove the circuit classification markings of the equipment per Sec. 725.124 and follow all C1 wiring methods. The one I am struggling with is the communications circuit (it is not a PoE circuit, just a plain old data cable). The best I can come up with is Exception No. 3 of Sec. 800.133, which leads you to Sec. 620.36. To me this says you can do it as long as your communications wire is rated the same as your Class 1 wire. Where I am doubting this is that Art. 620 deals with Elevators, Dumbwaiters, Escalators, Moving Walks, Platform Lifts, and Stairway Chairlifts. So what takes precedence? The fact that Code exists that allow for the combining of communications & Class 1 or the equipment listed in the title of Art. 620? Is my interpretation correct regarding the reclassification of C2 circuits per 724.130?[/FONT]
Any advice would be appreciated.
To try an stem off the same off topic responses I received in other forums.
Yes I know it is a class 1 div 1 location, or at least we pass through it.
Yes the cat 5 cable is rated for hazardous locations.
Yes the work requires a permit.
No the canopy lights circuits are not in the conduit going to the dispenser.
We don't need to hire a qualified electrical sub contractor or an electrical engineer for the work. (this was my favorite)
I am sure there are wireless intercom systems available, but that is not what I am asking about.
The reclassified circuits do have functional association with the c1 circuit in the fact that the intercom and data component of the dispenser are integral components of the same UL listed assembly, ie.. they make up the entire dispenser.
The cost of adding additional conduits to the dispenser is on average 20K, and yes we would love to do it as a change order for every single job. I just want a code reference or some type of backing that says we can or can't do it.
Here are my code citations (from 2014)
NEC 2014 800.133
800.133 Installation of Communications Wires, Cables, and Equipment. Communications wires and cables from the protector to the equipment or, where no protector is required, communications wires and cables attached to the outside or inside of the building shall comply with 800.133(A) and (B).
(A) Separation from Other Conductors.
(1) In Raceways, Cable Trays, Boxes, Cables, Enclosures, and Cable Routing Assemblies.
(a) Optical Fiber and Communications Cables. Communications cables shall be permitted in the same raceway, cable tray, box, enclosure, or cable routing assembly with cables of any of the following:
(1) Nonconductive and conductive optical fiber cables in compliance with Parts I and V of Article 770
(2) Community antenna television and radio distribution systems in compliance with Parts I and V of Article 820
(3) Low-power network-powered broadband communications circuits in compliance with Parts I and V of Article 830
(b) Other Circuits. Communications cables shall be permitted in the same raceway, cable tray, box, enclosure, or cable routing assembly with cables of any of the following:
(1) Class 2 and Class 3 remote-control, signaling, and power-limited circuits in compliance with Article 645 or Parts I and III of Article 725
(2) Power-limited fire alarm systems in compliance with Parts I and III of Article 760
(c) Class 2 and Class 3 Circuits. Class 1 circuits shall not be run in the same cable with communications circuits. Class 2 and Class 3 circuit conductors shall be permitted in the same cable with communications circuits, in which case the Class 2 and Class 3 circuits shall be classified as communications circuits and shall meet the requirements of this article. The cables shall be listed as communications cables.
Exception: Cables constructed of individually listed Class 2, Class 3, and communications cables under a common jacket shall not be required to be classified as communications cable. The fire-resistance rating of the composite cable shall be determined by the performance of the composite cable.
(d) Electric Light, Power, Class 1, NonPower-Limited Fire Alarm, and Medium-Power Network-Powered Broadband Communications Circuits in Raceways, Compartments, and Boxes. Communications conductors shall not be placed in any raceway, compartment, outlet box, junction box, or similar fitting with conductors of electric light, power, Class 1, nonpower-limited fire alarm, or medium-power network-powered broadband communications circuits.
Exception No. 1: Where all of the conductors of electric light, power, Class 1, nonpower-limited fire alarm, and medium-power network-powered broadband communications circuits are separated from all of the conductors of communications circuits by a permanent barrier or listed divider.
Exception No. 2: Power conductors in outlet boxes, junction boxes, or similar fittings or compartments where such conductors are introduced solely for power supply to communications equipment. The power circuit conductors shall be routed within the enclosure to maintain a minimum of 6 mm (0.25 in.) separation from the communications circuit conductors.
Exception No. 3: As permitted by 620.36.
NEC 2014 620.36
620.36 Different Systems in One Raceway or Traveling Cable. Optical fiber cables and conductors for operating devices, operation and motion control, power, signaling, fire alarm, lighting, heating, and air-conditioning circuits of1000 volts or less shall be permitted to be run in the same traveling cable or raceway system if all conductors are insulated for the maximum voltage applied to any conductor within the cables or raceway system and if all live parts of the equipment are insulated from ground for this maximum voltage. Such a traveling cable or raceway shall also be permitted to include shielded conductors and/or one or more coaxial cables if such conductors are insulated for the maximum voltage applied to any conductor within the cable or raceway system. Conductors shall be permitted to be covered with suitable shielding for telephone, audio, video, or higher frequency communications circuits.
NEC 2014 article 725.130
725.130 Wiring Methods and Materials on Load Side of the Class 2 or Class 3 Power Source. Class 2 and Class 3 circuits on the load side of the power source shall be permitted to be installed using wiring methods and materials in accordance with either 725.130(A) or (B).
(A) Class 1 Wiring Methods and Materials. Installation shall be in accordance with 725.46.
Exception No. 1: The ampacity adjustment factors given in 310.15(B)(3)(a) shall not apply.
Exception No. 2: Class 2 and Class 3 circuits shall be permitted to be reclassified and installed as Class 1 circuits if the Class 2 and Class 3 markings required in 725.124 are eliminated and the entire circuit is installed using the wiring methods and materials in accordance with Part II, Class 1 circuits.
Informational Note: Class 2 and Class 3 circuits reclassified and installed as Class 1 circuits are no longer Class 2 or Class 3 circuits, regardless of the continued connection to a Class 2 or Class 3 power source.
The company I work for does service work at retail gas stations, specifically the pump and tank work. We have two electricians on staff for service/small job work. No real heavy electrical work, when we build a new station we sub out the electric. One of the tasks our electricians perform on a routine basis is to replace the gas dispensers with new models. The challenge we come up against quite frequently at older stations is there is only on conduit to the gas dispenser. A modern gas dispenser needs three circuit types, a Class 1 for the power, a Class 2 or 3 for the intercom, and a communications circuit in the form of Cat. 5 cable rated for a hazardous location. My question has to do with combining all three circuit types into that one conduit. I think it can be done per code, but can someone confirm? Here is why I think it can be done:
[FONT=verdana, geneva, lucida, lucida grande, arial, helvetica, sans-serif]The Class 2/3 circuit can be reclassified and combined in a raceway with a Class 1 circuit per Sec. 725.130 as long as you remove the circuit classification markings of the equipment per Sec. 725.124 and follow all C1 wiring methods. The one I am struggling with is the communications circuit (it is not a PoE circuit, just a plain old data cable). The best I can come up with is Exception No. 3 of Sec. 800.133, which leads you to Sec. 620.36. To me this says you can do it as long as your communications wire is rated the same as your Class 1 wire. Where I am doubting this is that Art. 620 deals with Elevators, Dumbwaiters, Escalators, Moving Walks, Platform Lifts, and Stairway Chairlifts. So what takes precedence? The fact that Code exists that allow for the combining of communications & Class 1 or the equipment listed in the title of Art. 620? Is my interpretation correct regarding the reclassification of C2 circuits per 724.130?[/FONT]
Any advice would be appreciated.
To try an stem off the same off topic responses I received in other forums.
Yes I know it is a class 1 div 1 location, or at least we pass through it.
Yes the cat 5 cable is rated for hazardous locations.
Yes the work requires a permit.
No the canopy lights circuits are not in the conduit going to the dispenser.
We don't need to hire a qualified electrical sub contractor or an electrical engineer for the work. (this was my favorite)
I am sure there are wireless intercom systems available, but that is not what I am asking about.
The reclassified circuits do have functional association with the c1 circuit in the fact that the intercom and data component of the dispenser are integral components of the same UL listed assembly, ie.. they make up the entire dispenser.
The cost of adding additional conduits to the dispenser is on average 20K, and yes we would love to do it as a change order for every single job. I just want a code reference or some type of backing that says we can or can't do it.
Here are my code citations (from 2014)
NEC 2014 800.133
800.133 Installation of Communications Wires, Cables, and Equipment. Communications wires and cables from the protector to the equipment or, where no protector is required, communications wires and cables attached to the outside or inside of the building shall comply with 800.133(A) and (B).
(A) Separation from Other Conductors.
(1) In Raceways, Cable Trays, Boxes, Cables, Enclosures, and Cable Routing Assemblies.
(a) Optical Fiber and Communications Cables. Communications cables shall be permitted in the same raceway, cable tray, box, enclosure, or cable routing assembly with cables of any of the following:
(1) Nonconductive and conductive optical fiber cables in compliance with Parts I and V of Article 770
(2) Community antenna television and radio distribution systems in compliance with Parts I and V of Article 820
(3) Low-power network-powered broadband communications circuits in compliance with Parts I and V of Article 830
(b) Other Circuits. Communications cables shall be permitted in the same raceway, cable tray, box, enclosure, or cable routing assembly with cables of any of the following:
(1) Class 2 and Class 3 remote-control, signaling, and power-limited circuits in compliance with Article 645 or Parts I and III of Article 725
(2) Power-limited fire alarm systems in compliance with Parts I and III of Article 760
(c) Class 2 and Class 3 Circuits. Class 1 circuits shall not be run in the same cable with communications circuits. Class 2 and Class 3 circuit conductors shall be permitted in the same cable with communications circuits, in which case the Class 2 and Class 3 circuits shall be classified as communications circuits and shall meet the requirements of this article. The cables shall be listed as communications cables.
Exception: Cables constructed of individually listed Class 2, Class 3, and communications cables under a common jacket shall not be required to be classified as communications cable. The fire-resistance rating of the composite cable shall be determined by the performance of the composite cable.
(d) Electric Light, Power, Class 1, NonPower-Limited Fire Alarm, and Medium-Power Network-Powered Broadband Communications Circuits in Raceways, Compartments, and Boxes. Communications conductors shall not be placed in any raceway, compartment, outlet box, junction box, or similar fitting with conductors of electric light, power, Class 1, nonpower-limited fire alarm, or medium-power network-powered broadband communications circuits.
Exception No. 1: Where all of the conductors of electric light, power, Class 1, nonpower-limited fire alarm, and medium-power network-powered broadband communications circuits are separated from all of the conductors of communications circuits by a permanent barrier or listed divider.
Exception No. 2: Power conductors in outlet boxes, junction boxes, or similar fittings or compartments where such conductors are introduced solely for power supply to communications equipment. The power circuit conductors shall be routed within the enclosure to maintain a minimum of 6 mm (0.25 in.) separation from the communications circuit conductors.
Exception No. 3: As permitted by 620.36.
NEC 2014 620.36
620.36 Different Systems in One Raceway or Traveling Cable. Optical fiber cables and conductors for operating devices, operation and motion control, power, signaling, fire alarm, lighting, heating, and air-conditioning circuits of1000 volts or less shall be permitted to be run in the same traveling cable or raceway system if all conductors are insulated for the maximum voltage applied to any conductor within the cables or raceway system and if all live parts of the equipment are insulated from ground for this maximum voltage. Such a traveling cable or raceway shall also be permitted to include shielded conductors and/or one or more coaxial cables if such conductors are insulated for the maximum voltage applied to any conductor within the cable or raceway system. Conductors shall be permitted to be covered with suitable shielding for telephone, audio, video, or higher frequency communications circuits.
NEC 2014 article 725.130
725.130 Wiring Methods and Materials on Load Side of the Class 2 or Class 3 Power Source. Class 2 and Class 3 circuits on the load side of the power source shall be permitted to be installed using wiring methods and materials in accordance with either 725.130(A) or (B).
(A) Class 1 Wiring Methods and Materials. Installation shall be in accordance with 725.46.
Exception No. 1: The ampacity adjustment factors given in 310.15(B)(3)(a) shall not apply.
Exception No. 2: Class 2 and Class 3 circuits shall be permitted to be reclassified and installed as Class 1 circuits if the Class 2 and Class 3 markings required in 725.124 are eliminated and the entire circuit is installed using the wiring methods and materials in accordance with Part II, Class 1 circuits.
Informational Note: Class 2 and Class 3 circuits reclassified and installed as Class 1 circuits are no longer Class 2 or Class 3 circuits, regardless of the continued connection to a Class 2 or Class 3 power source.