I have a 10KVA high leg delta SDS. The secondary lands in a 30A fused disco fused at 20A. This serves two 20A 3 phase twist lock receptacles in which lathes will be utilized. The lathes have a cord connected 120v digital readout.

Is it permissible to pull a nuetral and install two 120v receptacle on this circuit? Both the three phase receptacles and the single phase receptacles will be protected by the three pole fused disco.
 