Yesterday I saw an interesting temporary power pole. There was a 20A 240V NEMA 6-20R receptacle fed by a 20/2 GFCI circuit breaker. The green ground wire from the 240V receptacle grounding terminal was connected to the neutral terminal of the 20/2 GFCI CB. The receptacle is 240V 2P-3W and has no neutral. It looked like it had been that way for a very long time. What do Y'all think?
 

kwired

Electron manager
Location
NE Nebraska
Unless that receptacle yoke is isolated from grounded objects, this should instantly trip the GFCI because of neutral to ground fault.
 

kwired

Electron manager
Location
NE Nebraska
I don't think so in this case since there is no neutral load and the GFCI is a 2-pole.
Would entirely depend if the GFCI:
1) monitors neutral
2) if 1) is true - if it has neutral -ground detection. If not it will need 4-6 mA fault current before it will trip.

Sound like it does have 1) but not certain about 2).
 