Is that one panel per meter or two?

Is the SEU supplying one or both meters? ...one or two panels?
 
"1 drop feeds 2 meters and 2 - 150 amp panel box one for each meter.
Still need the calculated load to be certain. If you go with full 300A, you're looking at 250kcmil copper, 350kcmil aluminum... assuming yes answer to next question.

Also, is this for a two-family dwelling service? [310.15(B)(7)]
 