120% rule for two Inverter outputs vs sup-panel
I was asked if you can use two 20a breakers in the 200 amp service instead of adding a sub-panel to combine both inverter outputs in to one feeder to the service with a 40a main and still use the 120% rule on the bus rating. This would be at opposite end of the main and the service has room for 2-2 pole breakers. My first taught was no that would go to 100% of the bus rating and looking at the nec 705 I can't find anything that says I have to do 100% so that leads me to say yes you can use the 120% of bus rating rule if on opposite end of the main breaker. What are your taught on this. Thank You :happyno::happyyes:
Physically it would be OK but check with your AHJ to see if they will allow two points of interconnection in the MDP.
It's code compliant and I have done many like this, but I have heard some AHJs have issues with it.
I concur with the other comments. What might trip you up is if an AHJ thinks they are one 'source' that requires a dedicated breaker according to 705.12(D)(1). But I have not had this problem myself. Just say they are two sources. :thumbsup:
What makes the most difference here is that the PV breakers are on opposing sides of the bus. For example, occupying #39-41 and #40-42 in a 42 space panel.
I don't see an issue with that since there won't be any loads between the two interconnection points.
NEC2014 revised the language of this, so that it is "125% of the total connected inverter output current", instead of the breaker rating (or sum of the breaker rating). This now prevents "round up errors" when sizing that interconnection breaker from being a showstopper, and it also justifies any mix of breakers for the solar interconnection at the opposite end of the busbar from the main supply, provided that (125% of all inverter current + Main Supply OCPD) <= 120% of busbar rating.
120% off bus bar rating
All this came from one of my ex-students that was installing 30 micro-inverters on two different roof levels 15 on one roof and 15 on the other roof same house same service and wanted to run the 2 raceway to the service instead of installing a sub-panel. The utility does not require a separate disconnect at this house. My local utility requires a utility disconnect so I have used a sup-panel to meet this requirement.
What do I need code for? What's the difference between a 2-pole 40A PV breaker and qty (2) 2-pole 20A breakers plugged onto the same stabs with identical contacts?
Are you talking about a quad that takes up 4 spaces, 4-poles, 2 on each side, or a quad that takes up 4 spaces, 4 poles, all on the same side, i.e. vertically in normal panel orientation? I'd reject the latter.
Regarding 40A, I thought we are doing two inverters, 4 conductors...???
I'm talking about a quad that takes up 2 spaces, 4 poles, like this one. Get it now? The point about 40A is that the panelboard would never 'know' the difference between this breaker assembly and a 40A 2-pole one.
Okay... got it. A 2-pole tandem... not what I call a quad though it does have 4 effective poles (2x2). The 2P tandem I'd pass as long as the panel listing designates the last two spaces on either side as useable for tandem breakers.