voltage tester was picking up voltage on a detached wire

Status
Not open for further replies.
Home inspector's question:

Can anyone explain why my voltage tester was picking up voltage on a detached wire in the panel? The tester's sensitivity range is 50V-1000V. Can detached wires have voltage over 50V?




http://www.kleintools.com/catalog/electrical-testers/non-contact-voltage-tester
 

Attachments

  • DSC03243.jpg
    DSC03243.jpg
    123.5 KB · Views: 2
Put a working incandescent light bulb across the black & white then black & grounding then grounding & White. If either one lights up you have an energized NM cable. If it does not light up and your pocket tester does not light up then it is a ghost/phantom voltage.
 
Put a working incandescent light bulb across the black & white then black & grounding then grounding & White. If either one lights up you have an energized NM cable. If it does not light up and your pocket tester does not light up then it is a ghost/phantom voltage.
Look at the picture in the OP and think about the advice you are giving.
 
What is on the other end of the cable being tested?

Could be connected to a breaker in the panel and the cable shown was a second homerun pulled by mistake.
Sot of like a ring circuit.
But that's just a possibility...
 
If I knew why I might could answer "why not"!
I'm asking why a HI might need to?

Well how would you check for double taps and other issues without opening the panel?

As far as being barehanded that is likely a safety violation but are we going to hold HIs to higher standard than ourselves?:)
 
Better question....
Why is the OP, as a HI, using a noncontact tester in a live panel?



I think Little Bill has a point, it's not really part of their job. They open the panel for a visual inspection and if they see anything questionable they should write it up.

Electricians shouldn't get upset when they see something like this on a home inspection report. You have cable in a live panel that's not capped off or taped.
 
I think Little Bill has a point, it's not really part of their job. They open the panel for a visual inspection and if they see anything questionable they should write it up.

Electricians shouldn't get upset when they see something like this on a home inspection report. You have cable in a live panel that's not capped off or taped.

I am at a loss why you would think an HI should not be using a non-contact tester. I am willing to bet it is in their training to do so.


Of course I have never understood the animosity between electricians and HIs. :)
 
Well how would you check for double taps and other issues without opening the panel?

As far as being barehanded that is likely a safety violation but are we going to hold HIs to higher standard than ourselves?:)

I was trying to avoid the "double tap" subject here but that's my point. What's the tester got to do with checking that?

Seems you have your "arguing britches" on today!:p
 
I was trying to avoid the "double tap" subject here but that's my point. What's the tester got to do with checking that?

Is there a reason they should not use a tester if they see something odd?

Seems you have your "arguing britches" on today!:p

:lol::lol:

I am working really odd schedules lately and right now I am board out of my mind.
 