Separate phases in separate conduits.......and # wires per lug....

Status
Not open for further replies.

dionysius

Senior Member
Location
WA
1200 A to be run from 1000kVA 480Y/277 utility XFR SEC to SWBRD.
Breaking it up into 4 x 300A parallel runs.
So using 4 PVC Sched 80 conduits which will be located beside each other and underground.

Question A
Can the separate phases occupy same conduit???? :?
In other words:
Can all phase A be in first conduit?
All phase B in second conduit?
All phase C in third conduit?
All neutrals in fourth conduit?

I believe I have seen this allowed per NEC if conduit is plastic.
It would make for very neat and organized wiring.


Question B
Are two wires allowed per lug???:?
 

dionysius

Senior Member
Location
WA

What a beautiful picture. Tres magnifique!!!!! Thank you Sir.

I will check with Inspector before I implement. From a technical standpoint I see no problem as long as the conduits are close together as in pic for electrical field containment.

When is firestop or water sealant required in such an installation???? Anybody know??? Any conduit termination bushings specified by NEC as shown here. Why not just the plain plastic cleanly cut in such a terrain vertical install.
 

iwire

Moderator
Staff member
Location
Massachusetts
What a beautiful picture. Tres magnifique!!!!! Thank you Sir.

I will check with Inspector before I implement. From a technical standpoint I see no problem as long as the conduits are close together as in pic for electrical field containment.

When is firestop or water sealant required in such an installation???? Anybody know??? Any conduit termination bushings specified by NEC as shown here. Why not just the plain plastic cleanly cut in such a terrain vertical install.

There are tight limitations on doing this.

Also keep in mind that four current carrying conductors in a single conduit requires derating.
 