When I reference "conduit fill charts NEC" on google, the first 10 charts that populate all differ from the informative annex C in NFPA 70 2014. For example, 1/2 EMT per NFPA70 annex C table C.1 I can fit 2 #8AWG conductor in a 1/2" EMT.
When I type "Conduit fill chart NEC" into google, the first 10 charts that come up say I can fit 3 #8AWG in a 1/2" EMT. When did this change and why?
Also, do the conductors in the fill charts include the ground conductor, or only current carrying conductors?