Is there, (should there) a swimming pool section? With the amount of information now available from this site... it's a very valuable resource.
I am one of those ... I liked it much better way back when there was only one forum.There is not a pool section and IMO that is not a bad idea but some feel that we have too many sections already. It would only help organize things better
I am one of those ... I liked it much better way back when there was only one forum.
I am one of those ... I liked it much better way back when there was only one forum.
What do you mean by totally isolated from the grid?After watching the MH video's.... I'd like to remove my 120volt lights, and change them all to low voltage. Totally isolated from the grid. Is there is a good read on it? I don't get involved in pool work at all, and this would be all new to me. I usually deal with light commercial.
I only view the forum by having it show me the new posts....That makes it work like a single forum for me.I am surprised about this Don. I assume you have your computer files organized where you can find them. If I want to read questions about pools then you just need to go to that forum. On my computer I have a folder with all the pool files in it-- no different IMO. The search feature has a lot to be desired so I avoid using it.
I am one of those ... I liked it much better way back when there was only one forum.
What do you mean by totally isolated from the grid?
One of the most important things to know about swimming pools is the importance of equipotential bonding. Leave nothing conductive within the pool or within reach of users unbonded.
The intent of this bonding is not to earth things, it is to bring everything within the user's reach to same potential so the user will not be subject to any voltage. Say there is a small voltage drop on the service neutral - your equipment grounding conductors are all bonded to that service neutral and will all see that voltage drop on the service neutral but as a rise above earth potential. So if you have an isolated conductive light shell it will be at earth potential but the rest of your equipotential system is at the service neutral voltage, users that touch or approach the light shell will get shocked even though it is isolated from the grid, because true ground potential is lower then the rest of the pool equipment.
If you bring an equipment grounding conductor to the pool lights, regardless of the operationg voltage and even if you never turn the power to the lights on, you just brought that 1 or 2 volts potential to ground to your pool area. If everything conductive in the pool area isn't bonded to bring it all to same potential you will have voltage present between any bonded and non bonded objects. Bond everything but forget to bond a metal structure for a diving board and you now have that 1 or 2 volts between everything bonded and that diving board structure that is at earth potential.Let's say my house / pool equipment is 300' from the POT. The service neutral will be 1 or 2 volts above ground. I understand that. But now I'm reading to change all the pool lights to low voltage, with an isolation transformer. This is where I get lost.... with the theory.
Because any one object that is connected to an EGC will introduce a hazard possibly to the entire pool. Number one item is a pump. This pump can possibly raise the potential of the entire body of water above earth potential.ok, then why run a ground wire to any light niche? Why not let it sit at earth voltage, rather than introducing neutral voltage ?
I'm working on a house, not the pool equipment. But I looked at the pool equipment, and I saw the pump is not bonded. The lug is not connected to anything.
Where does the equip-bond normally come back to? Is there a designated location?
680.26(B)(6)(a) Double-Insulated Water Pump Motors. Where a
double-insulated water pump motor is installed under the provisions
of this rule, a solid 8 AWG copper conductor of sufficient
length to make a bonding connection to a replacement
motor shall be extended from the bonding grid to an accessible
point in the vicinity of the pool pump motor. Where there
is no connection between the swimming pool bonding grid
and the equipment grounding system for the premises, this
bonding conductor shall be connected to the equipment
grounding conductor of the motor circuit.