jaylectricity
Senior Member
- Location
- Massachusetts
- Occupation
- licensed journeyman electrician
Right now there's a 480V three phase service. Main panel has service disconnect and 8 circuit breakers rated 200, 400, or 600 amps. Two of the breakers feed step-down transformers. One feeds 208/120v three phase panel while the other feeds a 240/120 single phase panel. From each of these panels there are feeders to various panels throughout the building. I've eliminated the need for any of the three phase sub-panels.
We want to remove all the equipment and replace with a 5 position meter bank. The project will take a few days at least, but I need to keep power to the building for business operations. Half of the floor space is in use, but over half of that is just warehouse with LED lighting and a handful of fans and a garage door opener. The other half is office space with LED lighting, a dozen computers and two HVAC units drawing about 10kva total.
With a proper calculation would I be able to get a temporary service to a single meter mounted on the building capable of carrying that kind of load? Or is that too much demand for a temporary service? I have always thought of temp services as a pole mounted meter with a few breakers and some gfci receptacles that you install while a building is being constructed.
If I could feed the one single phase panel I could remove a lot of the equipment and allow construction to be planned for a retail space without the new service being imperative to being finished any time soon.
We want to remove all the equipment and replace with a 5 position meter bank. The project will take a few days at least, but I need to keep power to the building for business operations. Half of the floor space is in use, but over half of that is just warehouse with LED lighting and a handful of fans and a garage door opener. The other half is office space with LED lighting, a dozen computers and two HVAC units drawing about 10kva total.
With a proper calculation would I be able to get a temporary service to a single meter mounted on the building capable of carrying that kind of load? Or is that too much demand for a temporary service? I have always thought of temp services as a pole mounted meter with a few breakers and some gfci receptacles that you install while a building is being constructed.
If I could feed the one single phase panel I could remove a lot of the equipment and allow construction to be planned for a retail space without the new service being imperative to being finished any time soon.