ntr
- Netherlands
Hi all,
In a control panel for air cond. and refr. equipment as per UL508A I have to provide branch circuit protection and switching on/off for 6 of these water pumps (see image below). They have to be switched on and off simultaneously. Is it possible to use one inv. time circuit breaker and contactor for all these pumps as per 31.4 a) branch protection for motor groups? The UL508A is not very instructive. As far as I understand you have to comply with NEC (2014) article 430.53 (D) and 430.53 (A). In 430.53 (A) there is a reference to 430.32 (B) (4) Impedance-Protected. But i'm not sure what is meant by "if the motor is part of an approved assembly...". Can someone clarify if one CB is sufficient?
Thanks.
Nico
Thanks.
Nico