Jon456 Senior Member Location Colorado Jun 23, 2016 #1 I have never seen one but I apparently need some. Would it require a special load center or would it use a pig-tail like a GFCI/AFCI breaker?
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician Jun 23, 2016 #2 It's called a switched neutral breaker. It looks like a two pole gfci breaker but there is no test button. You don't need a special panel to use them.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jun 23, 2016 #4
drcampbell Senior Member Location The Motor City, Michigan USA Occupation Registered Professional Engineer Jun 24, 2016 #5 When is a switched-neutral breaker called for?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jun 24, 2016 #6 drcampbell said: When is a switched-neutral breaker called for? Click to expand... The most common area I can think of is gas dispensers (514.11).
charlie b Moderator Staff member Location Lockport, IL Occupation Retired Electrical Engineer Jun 24, 2016 #7 During my short career in the Naval Architecture and Marine Engineering business, we used them in the design and construction of tanker vessels. I am curious as to why you are being required to supply them for your project. Can you elaborate?