225.30 ..... Would this apply to a pool house?
dcooper
Ma
I'm reading this and thinking if you have 2 cir supplying a pool (pump and light) in a pool house ..... You need a sub panel?
Can you explain?
The section you've mentioned states that a MWBC will be considered a single circuit so if you had a 1Ø system you could run a 3-wire MWBC (2 circuits) or as Bob stated for a 3Ø system you could run a 4-wire MWBC (3 circuits) and still comply.
II. Buildings or Other Structures Supplied by a
Feeder(s) or Branch Circuit(s)
225.30 Number of Supplies. A building or other structure
that is served by a branch circuit or feeder on the load side
of a service disconnecting means shall be supplied by only
one feeder or branch circuit unless permitted in 225.30(A)
through (E). For the purpose of this section, a multiwire
branch circuit shall be considered a single circuit.