K8MHZ
Senior Member
- Occupation
- Electrician
The OP has not mentioned jumpers and it would be illogical for them to have been installed.
I am not buying it.
I agree it's not logical, but I have seen it.
Again, take a look at my bad sketches. The 'jumpering' is done ahead of the sub-panel, but I have seen it in the panel, too.
And where do you see the word 'jumper'?
The OP didn't mention it, but that's the only way to feed a 120/240 panel and get all the breakers to have 120 volts.
To each their own, I am not buying into your jumper theory.![]()
Or, a ungrounded conductor is open and the OP is reading the same leg on both sides of the breaker due to reading through loads.
That is common, much more so than some sub-panel rigged for 120 volt only.
Originally Posted by Mikros![]()
![]()
I have a Milbank meter/panel combo pedestal feeding a sub-panel. (240/120v 1-ph 3w)
In the Milbank pedestal panel, there is a 60A 2pole breaker that feeds a separate sub-panel next to it.
The 60A 2P breaker is installed in a position where the two poles are fed from the same leg in the Milbank panel. (so, 120v to ground on each pole, but basically zero volts between them)
My reading of the OP is the same as Iwire's and why I asked.
It's based on what Iwire posted:
Now tell me why on a new (assumed) meter/main combo someone would "jumper" the legs since 240V is right there. The bus in a meter/main is the same as any other bus or panel. So I can't see how a 2-pole breaker could possibly pick up the same leg on both poles.
That aside, I also think (like Iwire) that there is an open either in the bus stab or the 60A breaker.
Also haven't seen where the OP has come back to "clear up" any confusion.:happyno: