I have a single phase 400A service I installed on a new residence.
Out of the meter can is 2/0 thhn Cu supplying a 200A MB panel located immediately inside the dwelling.
Also out of the meter can is #1 thhn Cu supplying a 150A disconnect located immediately inside the dwelling.
From that disconnect I am traveling approx 100' via pvc pipe and 4 conductors to a main lug 150A rated panel at the opposite end of the house.
I say that the conductors traveling to the panel located at the opposite end of the house can be #1 thhn Cu.
A guy helping me out ( holds journeymens license ) says they should be 1/0.
I tell him that they don't need to be larger than what's feeding the disconnect.
He disagrees and says the #1 is only good for 130 A in that application.
Opinions please.