I need to provide optional standby power for a couple small loads. Does the transfer switch need to be specifically listed for this purpose? Would a double throw power relay be sufficient for this purpose?
Not to my knowledge.I'm not following. I used the term optional standby as referenced by article 702. The generator would be a portable unit. It would be started manually. This is a residential application. Main panel feeds a standby panel via DT relay. NC contact of DT relay connected to feeder. NO contact of DT relay connected to generator power inlet. DT common connected to standby panel main lugs. DT relay coil connected to generator power inlet.
Power goes out. Plug in generator. Start generator. DT relay disconnects utility feed to standby panel and then connects generator. I realize there are other possibilities. For the simplicity of the question let's assume the above configuration.
Does NEC code prohibit use of a double throw relay being used as a transfer switch for a optional standby applications?
I'm not following. I used the term optional standby as referenced by article 702. The generator would be a portable unit. It would be started manually. This is a residential application. Main panel feeds a standby panel via DT relay. NC contact of DT relay connected to feeder. NO contact of DT relay connected to generator power inlet. DT common connected to standby panel main lugs. DT relay coil connected to generator power inlet.
Power goes out. Plug in generator. Start generator. DT relay disconnects utility feed to standby panel and then connects generator. I realize there are other possibilities. For the simplicity of the question let's assume the above configuration.
Does NEC code prohibit use of a double throw relay being used as a transfer switch for a optional standby applications?
My mistake. When you said optional transfer switch, I assumed it was a commercial install, and there was also a required transfer switch.
Personally, I think using a DT relay has too much chance of backfeeding power back to the utility during if the relay failed to operate properly.
My local power company wouldn't allow it. See page 12 of this document for an example:'
https://ameren.com/-/media/corporate-site/Files/Reliability/SafeConnectDocumentC0Form.pdf
I would suggest sticking with a listed manual transfer switch. They aren't that expensive.