Shielded Cable for CT & PT Wiring

Status
Not open for further replies.

Sunny_92

Member
Location
York, PA
Is it typical to use shielded cable for CT and/or PT secondary wiring? I'm working on a design for a small substation and would like to get a better idea of when it's best practice to use shielded cable. Thanks!
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
I don't know what the code states but in all my 46yrs in the field I have never seen shielded cable in this application or any problems caused by not using it.
 
Shielded is typically used in extra high voltage substations (230kV and up), and sometimes in lower voltage subs for cap banks.

Sent from my XT1254 using Tapatalk
 