I have ran into a interesting scenario with a AHJ. i have always sized my solar back-feed breaker in a residential panel based on taking the main and /or the buss rating, multiplying by 120%, subtracting the main breaker and sizing the solar breaker accordingly - (ex. : 200a main x 120% = 240a less the main breaker - 40a back feed bkr). The AHJ has informed me that this calculation is WRONG !!! The AHJ does the calculation as follows : take the back-feed breaker and multiply by 120% then add the main breaker. If his amount is the same or less than the buss/ main rating than it is acceptable. (ex : 50a back feed x 120% = 60a + 200a main = 260a , main buss rating = 225a. this will not pass inspection)
My calculation was this : main buss - 225a x 120% = 270a - 200a main = 70a available for solar back-feed
AHJ calculation : 50a back-feed x 120% = 60a + 200a main = 260a to big for buss rating, need to reduce main to 150a and back feed to 40a
Am i missing something and what code articles can i base my argument on
Thx