Saturn_Europa
 - Fishing Industry
 - Electrician Limited License NC, QMED Electrician
The polymer room in my solids facility flooded today.  Unfortunately, the PLC/VFD control panel is inside the containment area.  Luckily the VFDs are lower than the PLC and when the VFDs blew up the operators responded to the alarm and found the flooded room.  A 3" schedule 80 PVC ball valve split in half, so it was quite the flood.
Installed new drives and set the parameters no problem and we all were standing around feeling proud of ourselves until we noticed the the Hertz were dead at the minimum VFD speed and would not speed up no matter the HMI set point.
I went online with the PLC and the program was calling for the drives to ramp up. After about 30-40 minutes it kind of dawned on me. New drives, new network card, I need to set the IP address and subnet. I'm old school and cut my teeth on 4-20 mA analog speed command and 4-20 mA speed feedback. Networking drives is brand new to me. Its compact logic to AB drives and the drives are right there in my RS Logix 5000 program but there is no communication of course.
I pulled up the manual and it said to download BOOTP server. When I launch BOOTP server, it opens correctly but there are no devices listed, and there are no MAC addresses listed. Do I need to set up my laptop to a specific IP address to be able to see the new drives? I tried to go through an unmanaged switch and also plug directly into the drive. Neither worked.
After wasting about 2 hours on it tonight I had to throw in the towel. I am hoping some of the VFD gurus on this site can point me in the right direction. Unfortunately, I do not have part numbers or model specs with me. All that stuff is at work.
Windows firewall is turned off. Do PowerFlex40s come with a default IP address?