During a site visit to a project, I noticed an MLO panel (PB) to have some circuit breakers above 6'-7", some up to +91". This panel is connected to the MDP in the same room, which has the panel PB disconnect at a proper height.
My question: Is View attachment 2552553panel PB violating the code? (section 404.8)
Side question: why place multi-pole breakers head-to-head? (Yes, I admit I don't know the amperages)
Since the OP's question has been answered, may I go off-topic and ask what would the issues be with head-to-head multi-pole breakers?Side question: why place multi-pole breakers head-to-head?
There is absolutely no problem if they're within the size range permitted by the manufacturer of the panel. Since they're connected to the same bus stabs the current on those stabs would be additive for both breakers. The stab may be only rated to carry 100 amps so installing 2-100 amp circuit breaker opposite each other could overload that stab. If that same stab had two opposite 50 amp breakers there would be no issues.Since the OP's question has been answered, may I go off-topic and ask what would the issues be with head-to-head multi-pole breakers?
Thank you. That makes sense. So the issue is not that they're multi-pole breakers per se, but that multi-pole breakers tend to have higher current ratings than single-pole breakers?There is absolutely no problem if they're within the size range permitted by the manufacturer of the panel. Since they're connected to the same bus stabs the current on those stabs would be additive for both breakers. The stab may be only rated to carry 100 amps so installing 2-100 amp circuit breaker opposite each other could overload that stab. If that same stab had two opposite 50 amp breakers there would be no issues.
Exactly.Thank you. That makes sense. So the issue is not that they're multi-pole breakers per se, but that multi-pole breakers tend to have higher current ratings than single-pole breakers?
Coppersmith, can you please elaborate a little more? ThanksA 30x36x12 platform will solve the problem.
If they actually are loaded to near capacity then you won't be seeing that many in a typical QO panel as it won't take many to exceed the capacity of the panel anyway. Next step up in Square D equipment is I line panel, where the breaker plugs directly to the main bus and not to a link from the main bus. I have installed I line panels with nothing less than a 100 amp breaker installed in the entire panel.Exactly.
We did a job where we had a large 3Ø panel with several 100 amp, 3-pole CB's. From the factory they came installed all on the left side of the panel. The guy who tied the panel in decided it would be neater if he moved 1/2 of them to the right side opposite the CB's on the left. The bus stabs were only rated for 125 amps creating a potential hazard.
I have installed a few.I have never seen an 84 cir panel...
A 30x36x12 platform will solve the problem.
Coppersmith, can you please elaborate a little more? Thanks
I've had to install platforms on generators numerous times as well and most times just had the manufacturer include a platform in their pricing.I’ve had to install RV step platforms at generators because the main was too high because of the belly tank.They have a handrail, and the inspectors were happy with it.
Out of 50+ installs, only had two inspectors say anything about requiring it!I've had to install platforms on generators numerous times as well and most times just had the manufacturer include a platform in their pricing.
Roger