Hawkeye Gabe
Member
- Location
 - Arizona
 
- Occupation
 - Project manager / Estimator / Foreman
 
I have a situation with the ground pig tails. We are using #12awg x 10” ground pig tails in our fixture j boxes. We pulled #10awg throughout lighting system (parking garage) for distance.
Inspector is saying the ground to the box needs to be the same size as run in conduit.
I can’t find anywhere that tells me that’s right
or wrong. I was thinking this could be a UL tested assembly with UL listed ground screws but can’t find that either. Can anyone help me out with this so we don’t have to drop 800 fixtures and install #10 ground?
Thank you
	
		
			
		
		
	
				
			Inspector is saying the ground to the box needs to be the same size as run in conduit.
I can’t find anywhere that tells me that’s right
or wrong. I was thinking this could be a UL tested assembly with UL listed ground screws but can’t find that either. Can anyone help me out with this so we don’t have to drop 800 fixtures and install #10 ground?
Thank you
				