what NEC article 2011 please.No height limit, it has to be on a GFCI period.
210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel. Ground-fault circuit-interruption for personnel
shall be provided as required in 210.8(A) through (C). The
ground-fault circuit-interrupter shall be installed in a
readily accessible location.
Informational Note: See 215.9 for ground-fault circuitinterrupter
protection for personnel on feeders.
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-
ampere receptacles installed in the locations specified in
210.8(A)(1) through (8) shall have ground-fault circuitinterrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas,
and areas of similar use
I agree 100% until that one night when your wife comes home on a snowy night and the garage door doesn't open because the GFCI tripped. There's no CMP at NFPA that handles wife complaints. It becomes a matter of how long you want to hear her complain about the garage door not openingNo height limit, it has to be on a GFCI period.
Not only the complaint, but it's actually your fault, even though someone else installed it. ☠I agree 100% until that one night when your wife comes home on a snowy night and the garage door doesn't open because the GFCI tripped. There's no CMP at NFPA that handles wife complaints. It becomes a matter of how long you want to hear her complain about the garage door not opening![]()
There actually is a height limit but it is not an exception to the GFCI requirment. The GFCI receptacle must be readily accessible so for the average person the maximum height is about 7'.
Yes exactly. If you want to install the GFCI protection at the receptacle in the ceiling adjacent to the door opener it would need to low enough that it can be reached from the floor for testing.Doesn't this just mean the gfi protection must be a cb or an accessible gfi outlet upstream of the ceiling outlet?
We a wood burning stove at home and I cut and split the wood for it.I agree 100% until that one night when your wife comes home on a snowy night and the garage door doesn't open because the GFCI tripped. There's no CMP at NFPA that handles wife complaints. It becomes a matter of how long you want to hear her complain about the garage door not opening![]()
Late 80's or early 90's I remember having a particular GDO receptacle on GFCI (even though not required), new house and was new door opener. It would trip the GFCI. Back then we didn't investigate we just put in additional GFCI's where needed and made the ceiling outlet non GFCI protected, it was allowed then. Don't know if there was actually something wrong with that unit or if they just weren't paying that close attention to leakage on something that wasn't seeing much application on GFCI's at that time.If you’re worried about that, install a GDO with battery backup.
FWIW, I’ve never had the GFCI on my GDO trip. Nuisance or otherwise.
Everybody needs a cord reel hanging from the garage ceiling.Yep, and I admit that I put a cord reel on the ceiling of my garage and plugged it into the other side of the garage door receptacle. That is a good reason why there's no exception here.