I’m going to be installing a service for a large flat corn storage bunk. I’m trying to do a load calc and have a few questions on this one. The bunk will have 8-10hp 3 phase motors operating on 480volts There is also a conveyer and a drive over that need to be ran to fill the bunk.
The conveyer has 1-30hp conveyer motor, 2- 2hp front and rear axle motors, all are 480v 3ph motors, it also has 1- 1/2hp hood actuator @ 115volt 1 ph, and 1-2hp 230v 1ph hydraulic motor. And also 2 400watt lights
the drive over has a 1-15hp conveyer motor, and 1-2hp hydraulic motor with a 30 minute duty rating, and 2-400 watt lights
first question I have is I’m planning on running my conveyer and driver over off one disconnect and breaker. How do I figure the load of these two pieces of equipment? Would I find my largest motor and multiply 1.25x whatever fla 4.30.250 gives me for a 30hp? Then find my continuous load x 1.25 + non continuous load. Find the sum of al these loads and then size my main disconnect ocpd using 240.6.?
How do I figure the load on the hood actuator? Would I use single phase motor chart in 430, or use the nameplate rating?
to size my ocpd and my disconnect for my conveyer/drive over would I find the largest motor on the equipment, use the fla found in the in 430.250 “3phase motor flat char” and multiply by 1.25? Then add the continuous loadx1.25 + the non continuous load. Side my ocpd using 240.6?