baquail2022
- 901 Memorial Dr Aubrey Tx
- Technology Advisor
Today's code calls for arc-fault breakers (outlets) in the kitchen as well. Although they are a necessity, arc fault breakers tend to degrade with constant, high usage such as found in a residential kitchen.
Most of today's modern refrigerators have a defrost heater which can pull similar amperage as a coffee maker (or more depending on size of the refrigerator) Defrost cycles usually last at least 30 minutes average. To put a refrigerator on one of the countertop circuits does not make any sense since small kitchen appliances (coffee maker, toaster, blender, crock pots, etc tend to draw 12 or more amps. If the defrost cycle starts when the coffee maker heater is still on, it can over time cause nuisance arc fault trips. The 2020 NEC code 210.52 B Exception 2, in my interpretation, is stating that a dedicated circuit SHALL be installed for each "specific appliance" which includes these larger refrigerators. Regardless most all manufacturers of these self defrosting refrigerators require a dedicated circuit to maintain warranty integrity. Am I correct that these refrigerators deserve a dedicated circuit?
In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
Exception No. 2: In addition to the required receptacles specified by 210.52, a receptacle outlet to serve a specific appliance shall be permitted to be supplied from an individual branch circuit rated 15 amperes or greater.