hitehm
- Las Vegas NV
I totally agree.And I still would have done as I said.
Yes, but he also has feeders in the conduit so he has hot conductors going and coming.The OP doesn't have a switch loop. He is running a wire from the new panel to the wire that used to be on a breaker in the old panel. One hot conductor.
I agree!Yes, but he also has feeders in the conduit so he has hot conductors going and coming.
Since the code section cited specifically says something about the grounded conductor "where used", and the grounded conductor isn't used in this case, I don't see how code requires you to run a grounded conductor for the branch circuits. Since the feeder grounded conductor is not used, I don't think you have to run it either.So why is a multi-pole contactor different from a feeder/branch circuit?
Seems to me if the neutral is not used in the subpanel (no AFCIs or GFCIs), 300.3(B) doesn't require it to be present in the conduit.
Cheers, Wayne
and the magnetic effects on that one hot conductor is offset by equal current being on the feeder that is also in the nipple.The OP doesn't have a switch loop. He is running a wire from the new panel to the wire that used to be on a breaker in the old panel. One hot conductor.
Seems to me that the code was changed not real long ago to require switch loops to have a neutral conductor run as well. I think this was to accommodate dimmer switches. I don't recall off the top of my head where this is, assuming my recollection is correct.I don't have my book, what code section applies to a 2-wire switch loop without a neutral?
You're correct that a neutral is required in some installations at a switch but not all. If there is a raceway where the neutral can be added later then a 2-wire switch loop is still permitted.Seems to me that the code was changed not real long ago to require switch loops to have a neutral conductor run as well. I think this was to accommodate dimmer switches. I don't recall off the top of my head where this is, assuming my recollection is correct.
It doesn't really affect me so I'm not all that up on it but I seem to recall seeing it as a change to the code at some point in the not too distant past.You're correct that a neutral is required in some installations at a switch but not all. If there is a raceway where the neutral can be added later then a 2-wire switch loop is still permitted.
404.2 Exception, 300,20(A).I don't have my book, what code section applies to a 2-wire switch loop without a neutral?
Where does it say that?You can't have hots and neutrals originating from different panels no matter the distance between panels. Never would be code compliant
Since 210.4(A) refers to where the the branch circuit originates, I don't think that argument flies. The ungrounded conductors of the branch circuit originate at the panel with their circuit breaker. If the neutral of the branch circuit isn't present in that panel, it can't originate there.In this particular case, I'd argue that even that doesn't apply. The hot and neutral _are_ originating from the same panel. Everything originates from the 'main' panel, the hot get split up in the 'sub' panel into multiple separate wires, which then _return_ to the main panel to continue on with their respective neutrals.
(A) Installation.
Neutral conductors shall not be used for more than one branch circuit, for more than one multiwire branch circuit, or for more than one set of ungrounded feeder conductors unless specifically permitted elsewhere in this Code.