Have data device that needs 1-1/4" EMT. Do they make 4" square box that has 1-1/4" KO's?\
The box has to accommodate 1G faceplate.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree, a common waste of money based on some awful old standard. Just like no more than 180° of bend in a run.
 

RCDD

New User
Location
Arizona
Occupation
Telecom Engineer
The 5" Square box is required due to the bend radius restrictions of Cat 6 and above cable. There are (2) MFG of the 5" SQUARE BOX. RANDL T-55017 - http://www.randl-inc.com/t55017box.html & Steel City http://tnb.com/pub/en/node/1861 - Also, most standards will also require an extension 5/8 single gang extension ring RANDL #D-51G058 https://www.platt.com/p/0776981/randl-industries/5-square-x-single-gang-extension-ring/rand51g058 & STEEL CITY http://tnb.com/ps/fulltilt/index.cgi?part=82C1G58&co=US.

The 1" vs. 1.25" conduit sizing is becoming a hot topic in structured cabling. The pathways should be future-proof, but of course, most EC in the project want to reduce the sizing for cost and labor. It's an uphill battle since cabling requirements are standards and not code.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
+ the 4-11/16 adds another can of worms IF its a fire rated wall......
The IBC permits the installation of unprotected steel outlet boxes not exceeding 16 sq. in within a rated wall assembly as long as the sum total area of openings (wall cutouts) for those boxes does not exceed 100 square inches for any 100 sq. ft. of wall.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
+ the 4-11/16 adds another can of worms IF its a fire rated wall......
The IBC permits the installation of unprotected steel outlet boxes not exceeding 16 sq. in within a rated wall assembly as long as the sum total area of openings (wall cutouts) for those boxes does not exceed 100 square inches for any 100 sq. ft. of wall.
Augie maybe you can clarify. Wouldn't that be 16 square inches for the actual opening cut into the drywall not the box within the wall? Wouldn't a 4" box with a 2 gang opening be the same as a 2 gang 4 11/16" box opening?
 

kwired

Electron manager
Location
NE Nebraska
The 5" Square box is required due to the bend radius restrictions of Cat 6 and above cable. There are (2) MFG of the 5" SQUARE BOX. RANDL T-55017 - http://www.randl-inc.com/t55017box.html & Steel City http://tnb.com/pub/en/node/1861 - Also, most standards will also require an extension 5/8 single gang extension ring RANDL #D-51G058 https://www.platt.com/p/0776981/randl-industries/5-square-x-single-gang-extension-ring/rand51g058 & STEEL CITY http://tnb.com/ps/fulltilt/index.cgi?part=82C1G58&co=US.

The 1" vs. 1.25" conduit sizing is becoming a hot topic in structured cabling. The pathways should be future-proof, but of course, most EC in the project want to reduce the sizing for cost and labor. It's an uphill battle since cabling requirements are standards and not code.
Yet there never room enough for bend radius of even a 3/4" raceway in many cases.
 