Hi there gentlemen,
I like to run this troubleshooting call through your minds, that I have just been involved with. Called out to a water department well pump station( very small building containing one large pump), where they lost power and when power came back on, the VFD drive was not operating( was powered up with display working would not operate motor, in manual or auto). Their concern was the fuses needed to be checked after checking the fuses and seeing they were good I went on to check the voltage. 480v between all phases, 280v to ground phasea A.B.C. Now all these readings were taken at the motor controller compartment where the VFD drive was located off the top of its disconnect.
Then I went to the buildings main disconnect and meter a 200amp service which i shut it down for more readings. Notice it a 4 wire service one with neutral markings also terminated like a neutral through the disconnect an meter socket. Took some more readings found 480 between all phases but then(now remember that the building load is disconnected) phase A 100v to neut/ground phase b 480v to neut/ground phase c 480 neut/ground.
But then when I turn the building back on adding the load to the service, my readings go to my original readings that I had at the VFD compartment,
480 volts phase to phase--280volt each phase to neut/ground in main disconnect. With this discrepancy in mind I told them to call the power company to check the transformer out.
Overview
All these readings at the main service disconnect.
building powered up-480volt phase to phase.... 280 volt phase A,B,C to neut/ground
building power down-480volt phase to phase....phase A 100 to voltsneut/ground phase B 480 to neut/ground phase C 480 to neut/ground
miscellaneous thoughts and information.
This service feeds a motor Control Center, then off one of the compartments feeds a 3 phase transformer for 208 and 120 Volt power panel for lights and plugs.
When the power company did arrive which I was not there for,it was explained to them that they had a "FAKE NEUTRAL" and there was no issue with the power quality.
So my own thoughts tells me that they must have a 480 volt grounded delta corner service.( wish I could have confirmed this with the utility). But why am I getting 100 volts on phase A when I should get zero is this possibility a ghost voltage, did use a fluke meter. And if my memory(been in the trade since 1990) serves me correct when I troubleshooted these types of services in the past even with the building load on or off line, I would get the same readings!
And does the code permit to have a "FAKE NEUTRAL"!!!
Can a utility just provide you with just three hots and no ground reference back to their transformer??
I think the utilities faking it(lol)
If you gentlemen can help me out to understand how a delta readings should take place with building load on or off . Trying to really understand why phase to neut/ground value is changing with the building load being on/off line.
Looking forward to your feedback gentlemen.