Customer called and reported they had felt electric shock in their swimming pool.
The pool is bonded per NEC; I checked water to deck, water to handrails, deck to handrails, pumps are bonded, lighting niche is bonded, etc.
I performed a battery of tests around the pool mostly checking for voltage between surfaces. The customer said before I came they had the power company out also. So I called the engineer to discuss what they had checked.
The short story is, the lighting niche has a lower resistance than the deck/water/handrails. The customer only felt electric shocks when swimming past the light. They did not feel any shock when entering/exiting the pool. I was only able to read 2v to ground, engineer said the day he came they read 7v to ground in the water around the light. This wasn't to the deck, but to plugged into an extension cord leading back to the house. Water to deck its 0v.
The engineer I spoke with said he and a 3rd party engineering firm have been conducting a variety of tests on pools in the area where customers reported electric shock over the last several months. He told me their conclusion is that all newly constructed pools should have a 4x4 or at least 6x6 wire mesh under the concrete. We talked for about an hour, and discussed a lot more in detail, but this was the short version of the story.
Their recommendation to customers has been A) tear up your pool deck and install a wire mesh/grid, or B) float the pool bond from the electrical system ground, and remove 120v lighting fixtures.
This is the first time I've encountered someone being shocked on a pool w/ what we assume to be proper 4-corner NEC bonding underneath. The resistance from water to deck is pretty consistent around the entire perimeter of the pool but it is about 10 ohms lower at the lighting niche according to my meter.
The pool is bonded per NEC; I checked water to deck, water to handrails, deck to handrails, pumps are bonded, lighting niche is bonded, etc.
I performed a battery of tests around the pool mostly checking for voltage between surfaces. The customer said before I came they had the power company out also. So I called the engineer to discuss what they had checked.
The short story is, the lighting niche has a lower resistance than the deck/water/handrails. The customer only felt electric shocks when swimming past the light. They did not feel any shock when entering/exiting the pool. I was only able to read 2v to ground, engineer said the day he came they read 7v to ground in the water around the light. This wasn't to the deck, but to plugged into an extension cord leading back to the house. Water to deck its 0v.
The engineer I spoke with said he and a 3rd party engineering firm have been conducting a variety of tests on pools in the area where customers reported electric shock over the last several months. He told me their conclusion is that all newly constructed pools should have a 4x4 or at least 6x6 wire mesh under the concrete. We talked for about an hour, and discussed a lot more in detail, but this was the short version of the story.
Their recommendation to customers has been A) tear up your pool deck and install a wire mesh/grid, or B) float the pool bond from the electrical system ground, and remove 120v lighting fixtures.
This is the first time I've encountered someone being shocked on a pool w/ what we assume to be proper 4-corner NEC bonding underneath. The resistance from water to deck is pretty consistent around the entire perimeter of the pool but it is about 10 ohms lower at the lighting niche according to my meter.