So, thinking to post a follow up to this thread, and assuming you have all been munching on popcorn and waiting for the next chapter of “The Customer says his Electricity is Too Good”…
As all suspected, the fault was/is on the POCO side for sure. As best I understand it, it was a stuck (presumably ON) capacitor (PF correction??). Stop reading now if you don’t want any more details.
I opened a ticket last night around 10PM, but nothing happened until a service tech showed up in a bucket truck this morning. He pulled the front of the outdoor meter panel and saw the same ~235 to 255 ish VAC, fluctuating more than he thought it should. After talking to each other for a little bit, and realizing that neither of us were complete nincompoops, he mentioned he wanted to check the output of the secondary (at the bushings) on the 25 kVA pole mounted transformer (replaced in spring 2020). Neither of us thought it would show anything different, but that’s where he thought he might look next (I guess to rule out problems with the underground lateral). But we all know that any problems there are going to cause
lower service voltage (L-L), not
higher.
Anyway…
He said he was going to try and reach it from my driveway because there was a lot of traffic on my 2 lane rural road.
I said yes, that’s because there is a detour of another road that is funneling more cars past my house than normal.
He laughed and said, yes it’s funny because that detour is some of our other crews working on some lines nearby.
Both of us starting thinking the same thing right away.
I said, “When did they start working on those primary lines”?
He said, “Yesterday”.
Then he said, “When did you first notice this problem”?
I said, “Yesterday”.
So then he jumped back in his truck and started looking up the locations of the nearest regulators or capacitor banks and getting on the phone/radio with the crew that was nearby. I am certain to have some of these details wrong, but from what he explained, while working on some nearby 3 phase lines (my road is fed from the “B” phase of those lines), the crews temporarily re-routed where they were fed from. And so, for the first time yesterday, my 7680 primary was getting sourced from a slightly different “path”. Sorry for the terrible explanation. But from this new source, it was now going thru a PF capacitor bank that my B phase was previously never fed from. Then somebody on his end looked up the cap on that B phase and it reported “ON” when it should not have been. So they sent somebody there to put it in manual and then turn it off (with a hotstick I guess??). He then said that would automatically generate a new ticket for somebody to go look at why that was not operating properly.
Anyway, that's what he tried his best to explain to me. But long story short, it's definitely on their end.
My service voltage is still a bit wonky, meaning up and down. I've not seen numbers like 264 anymore, but low 250s are common, and it dips under 240 as well. And it changes real quick sometimes, and not because any load kicked on or off in the house. That's what I'd like to see stop happening.
Kinda like this...
View attachment 2563139
Just as the mains jump 8 volts in the small gif above, you can see the lighting brighten a bit. I expect this was happening to everybody on this leg, maybe ~ 80 houses.
I will wait a day or 2 till they finish whatever they are doing nearby and hope they restore the original feed to my B phase.
Thanks all, and bonus points for reading all the way down to here