Try swapping that bus stab location for thermal-mag breakers only, and keep AFCI's off it.I will attempt your experiment
Presumably they have the same logic boards in them whether plug on neutral or not.Now that I think about it, I think all the too sensetive breakers lacked the pigtails. Maybe I'll try swapping with a pigtail type.
Ground fault devices only trip on downstream events, and can't detect anything upstream, much less smoldering bus stabs, high-impedance N-G leakage from charcoal outlets, or carbonized devices, typical in existing wiring.As far as not having GFP function I think that turns them into an overpriced thermal magnetic breaker.
I literally had the exact same problem last spring.I have been troubleshooting a house that was completely rewired this year. What I have discovered about this tripping issue has finally taken me to an area that I don't know what else I could do to mitigate this.
This is 1 Siemens 20A CAFCI Plug on neutral circuit breaker, feeding 10 receptacles in the living room.
I have replaced the breaker with a new one which did slow down the tripping to around 3 times a day. I noticed the code on the first one was A00 and the replacement is A03.
I have replaced all receptacles in the room with new 20A Leviton TR receptacles, verified all wiring and even tape wrapped receptacle for good measure.
I have removed all connected devices and Meggered circuit at 500V L-N L-G & G-N, all maxing out the meter at 500 Megaohms.
Resident claims she believes cooking on the stove in the kitchen, or her kids playing on their cell phones in the living room seem to be times it will trip.
Last night I plugged everything in and turned it on, TV, christmas tree, Cable box, device charges, modem etc. I then turned all 4 oven burners to low so they were all rapidly turning on an off, and sure enough after about 10 minutes click. Obviously the oven is on a completely different circuit.
This is where it gets real interesting, the cell phone suggestion. I have a friend rapid text me 10 times as I hold my cell phone next to the CB. And sure enough, on the 4th text it trips. This house is probably a 6th of a mile as a crow flies to a cell tower.
I guess my question is, where would one go from here? Is it even possible to mitigate the interference that could be causing this from a cellular signal? Or to somehow stop the feedback from the stove into the system?
Any input would be greatly appreciated as I feel I am running out of options.
Sorry I mispoke. The breakers that trip don't have a load terminal on them. I'll try swapping them with the type that have the load terminal. I'm not sure why some have terminals, but they might measure the neutral current and that might make them more accurate.Presumably they have the same logic boards in them whether plug on neutral or not.
Have also found bad power strips, including brand new ones trip GFCI with indicator light wired to ground.I'd say 50% if AFCI problems I find in new appliances are with that internal circuit.
Yes you are right, and is why the breaker in my situation actually tripped for a concerning situation - because it eventually developed a ground fault. An AFCI without GFP protection likely continues to hold just like a standard thermal mag breaker would have in that situation.Ground fault devices only trip on downstream events, and can't detect anything upstream, much less smoldering bus stabs, high-impedance N-G leakage from charcoal outlets, or carbonized devices, typical in existing wiring.
Tying to prove sustained arcs in residential applications is not the best function of AFCI's.
One AFCI trip function, which is ignored by GFCI's, can be demonstrate remotely with 1 hand.As far as not having GFP function I think that turns them into an overpriced thermal magnetic breaker.
I second thatIt's been shown that AFCI breakers are sensitive to RF signals, you can watch some demos of that on YouTube.
Unfortunately, I don't think that would help because the electronics inside GFCIs would need to have very narrow selectivity at the particular RF frequency band being used in order to distinguish one frequency from another. I think what's going on is that the semiconductor junctions inside the GFCI electronics are rectifying the RF, and thereby producing a signal that's proportional to the instantaneous amplitude (i.e., strength) of the RF signal. This would be just like a crystal set receiver where a diode detects AM broadcast signals. And so the the RF interference detected (i.e., demodulated) within the GFCI electronics can then cause it to trip. When you key up a two-way radio, the RF will suddenly come on, and that turn-on itself could create a step in a detected RF level which then trips the GFCI. I think the GFCI/AFCI manufacturers need to have more filtering and/or other measures to reduce their susceptibility to RF.IDK anything about RFI. Is it possible to change the frequency that the radios are using? Channels?
I second that. I had a situation in a Jersey City, NJ high rise apt. where the security guards claimed that each morning when they came in, the GFCI breakers for the de-icing equipment had tripped. I asked if they were using their walkie-talkies to communicate with the front desk when they were doing their rounds and they said yes. I proved this when I took one of their radios, went into one of the electrical closet and just keyed the mic. All (6) GFCI breakers tripped at once. All the branch circuit wiring was done in EMT. The guards are not going into electric closets on their rounds. However, if they are in the area of the de-icing cables and they key the mic on the radio, the cables act like an antenna and the breaker(s) will trip.
What does this have to do with ASFCI's ? I'm guessing that these breakers have similar electronics internally that are subject to RF interference in some way. I don't see any way you can protect the breaker from RF. Even if it were possible to "tin foil" them I believe the interference is coming back on the branch circuit wiring that is acting like an antenna. This i
At one time all AFCI's had GFP component to them just a 30 mA trip vs a 4-6 mA trip. That not the case for all of them anymore though. (Somehow can't get cursor outside of the "quote box" Phat fingers pressed some unknown key combination and here I am)