Does the amendment actually require a single receptacle?In NYC for window air conditioner. Local amendment.
CMP 2 has a published statement saying otherwise...it was in response to a proposal to require the use of a single receptacle where the code requires an individual circuit.Anytime you are required to provide an individual circuit to a cord and plug machine then that receptacle should be a single device. A built-in microwave requires a single receptacle in this area since the microwave calls for an individual circuit.
It was my recollection that a single receptacle isn't actually required but is considered to be a good practice.CMP 2 has a published statement saying otherwise...it was in response to a proposal to require the use of a single receptacle where the code requires an individual circuit.
Subsection 210.11 (C)(4) - Add a new subsection 210.11(C)(4)t oread as follows:Does the amendment actually require a single receptacle?
Not an interpretation ...a panel statement when they rejected a proposal that would have required the use of single receptacles for individual branch circuits.Subsection 210.11 (C)(4) - Add a new subsection 210.11(C)(4)t oread as follows:
(4) Air-Conditioning Branch Circuit. In addition to the number of branch circuits required by other parts of this section, an individual branch circuit shall be provided for each air-conditioning receptacle
required by 210.52(1).
I was not aware of cmp2 interpretation that individual branch circuit can have a duplex receptacle.
So it's up to the average everyday homeowners. Dad is an accountant and mom is a teacher, to know that they are not supposed to use the other receptacle. Brilliant!(2017) NEC definition: "Branch Circuit, Individual. A branch circuit that supplies only one utilization equipment." So you can use a duplex receptacle, and as long as you only plug in one thing, it's an individual branch circuit.
Cheers, Wayne
That's what breakers are for, if needed.So it's up to the average everyday homeowners. Dad is an accountant and mom is a teacher, to know that they are not supposed to use the other receptacle. Brilliant!
No different from the "no equipment ground" sticker required by 406.4(D)(2)(b). That is really a reference to 250.114 but no homeowner and few electricians know that.So it's up to the average everyday homeowners. Dad is an accountant and mom is a teacher, to know that they are not supposed to use the other receptacle. Brilliant!
Only in Ohio. Still not really 'required' unless you use the exceptions.A single receptacle is not required anywhere in a dwelling.
Don,Not an interpretation ...a panel statement when they rejected a proposal that would have required the use of single receptacles for individual branch circuits.
One issue is that to my understanding an individual branch circuit is allowed to have multiple receptacles in different locations, for the purpose of serving a specific mobile piece of equipment (e.g. a single welder). So the change would need to allow multiple single receptacles. Still no need for two receptacles (a duplex) in one location.Any idea why they rejected this proposal? I don't see a problem with requiring a single receptacle on an individual branch circuit.
I have no problem with that.So the change would need to allow multiple single receptacles.
(2011 code proposal)Don,