Timona
- Houston, Texas
- Graduate Electrical Design Engineer
I have a 4000A total load. How do I spec CT can meter for this? Project is in Palm beach FL. I have no clue because I have never done this before
Yeah typically I see requirements that customer provide a switchboard with metering section for anything over the 800-1000 amps range. I don't even think I've seen a CT cabinet over a thousand amps but maybe they are used in some placesI agree the POCO will tell you what's required. In NYC we use a meter section in from of the switchgear that has the CT's in it with a 10 conductor meter cable to the ten-point meter pan.
Nicely shapedHere's a 2000 amp CT section. 4000 amp is similar.
I believe XHHW.Also what insulation might those conductors be using
A pain to strip. How would the inspector see it? I prefer a few wraps down by the termination.I believe XHHW.
I have always wondered why stand alone CT cabinets seem to be the only equipment that has lashing requirements. Anyone seen it on panelboards or switchboards?I have only done a few CT setups, there was specific requirements for roping conductors. Not required here or not done yet? When you post quality pictures expect comments!
We never lash anything even 4000 amp services get zero lashing. We often do install some fiberglass strut to support the conductors with cable ties.I have always wondered why stand alone CT cabinets seem to be the only equipment that has lashing requirements. Anyone seen it on panelboards or switchboards?
Yet pretty much every CT can I have seen has that label requiring lashing, any idea why? Maybe one of those things that's been that way forever and no one knows why and no one wants to change?We never lash anything even 4000 amp services get zero lashing. We often do install some fiberglass strut to support the conductors with cable ties.
Yes I understand that, but what I don't understand is why the nearly universal requirement (presumably by the manufacturer?) for lashing in a CT cabinet, regardless of size or available fault current. Yet essentially no such requirement in other equipment.Lashing is keep the conductors secured during a short circuit. The high current results in magnetizing forces that can can cause conductor damage as the conductors try to straighten out.