I have a system with 4- 480V inverters that connect to a main PV panelboard. See the info below:
(2) 100K
Max output: 120.3A
OCPD: 175A
(2) 75K
Max output: 90.2A
OCPD: 125A
Main PV Panelboard OCPD: 600A
Main PV Feeder length: 630ft
Feeder conductors: 3 sets of 3/0 CU thwn
When the system is at full capacity, the main PV 600A breaker trips. With two DC switches off, which are 8 strings, the breaker stays. That is about 84% of the entire system.
This has happened from the initial start-up. We checked torque on the feeder connections and breaker to bussing connections.
A couple of the inverters can sometimes go into a "grid interference" alarm when the system is at full capacity.
I installed a data logger fluke 1730 meter the other day to test and troubleshoot. When the inverters were at full capacity, the peak amperage was 343A. The main 600A breaker tripped.
I've talked to the breaker seller, and he said we should replace it but that it may be too much heat on the breaker. The panelboard isn't in direct sunlight, although it gets hot here - 100°F plus. He was wondering about replacing it with a 700A instead. I have contemplated that since we are protected at the MSB by 600A fuses and a 600A breaker.
Any thoughts?
My initial is that it's a faulty breaker.
Oddly enough, when I was testing it with the fluke 1730 and it tripped, one of the inverters went dead and will not respond. I am in the RMA process for that with the inverter manufacturer.
Could harmonic distortion be an issue?
Sent from my SM-G998U using Tapatalk
(2) 100K
Max output: 120.3A
OCPD: 175A
(2) 75K
Max output: 90.2A
OCPD: 125A
Main PV Panelboard OCPD: 600A
Main PV Feeder length: 630ft
Feeder conductors: 3 sets of 3/0 CU thwn
When the system is at full capacity, the main PV 600A breaker trips. With two DC switches off, which are 8 strings, the breaker stays. That is about 84% of the entire system.
This has happened from the initial start-up. We checked torque on the feeder connections and breaker to bussing connections.
A couple of the inverters can sometimes go into a "grid interference" alarm when the system is at full capacity.
I installed a data logger fluke 1730 meter the other day to test and troubleshoot. When the inverters were at full capacity, the peak amperage was 343A. The main 600A breaker tripped.
I've talked to the breaker seller, and he said we should replace it but that it may be too much heat on the breaker. The panelboard isn't in direct sunlight, although it gets hot here - 100°F plus. He was wondering about replacing it with a 700A instead. I have contemplated that since we are protected at the MSB by 600A fuses and a 600A breaker.
Any thoughts?
My initial is that it's a faulty breaker.
Oddly enough, when I was testing it with the fluke 1730 and it tripped, one of the inverters went dead and will not respond. I am in the RMA process for that with the inverter manufacturer.
Could harmonic distortion be an issue?