480V 1phase circuit feeds 11 exterior locations. At each location is a hand hole with splices to feed an equipment box. The first component in the box is a breaker then on to a 480v to 120v step down transformer to the rest of the equipment in the box. At all 11 locations we opened the breaker. When we energized the circuit it popped the 400A breaker at the MDP.  When reset, the 400A breaker stated a GF had occurred. There is @ 20 feet of EMT inside the building before this circuit goes outside into the ground  routed through PVC pipe. Other than the EMT what would cause a ground fault to occur when all the loads are opened per their respective breaker? Full disclosure - all 11 hand holes are subject to filling up with water completely. 1 equipment box location had its bare ground wire severely corroded and the hand hole that fed it the bare wire was discolored red and broken in multiple places with approximately a 1 foot section of the ground rod having broken off.
Thanks.
			Thanks.