Hi, I'm bidding on a wiring job for a Cummins 20kW generator project for a single family residential home on Long Island. In my mind a #4 THHN wire would be sufficient because the generator output is only 83.3 amps. But a friend of mine who has wired a lot more generators with his boss said they use #2 THHN for a 20 kW. Now I'm second guessing myself and think I should quote #3 as I see a composite cable for that size generator is a number 3. Am I wrong to think #4 is correct?
Also, if anyone has any input for the control wiring that would be helpful. As I have only wired Kholer and Generac generators before.
Thank you,
K.R