wwhitney
- Berkeley, CA
- Retired
Thanks for your response, you have a nice way of summarizing things clearly, although I don't agree with the above.I tend to side with @jap that connecting a wire at the supply end only doesn't change this, but IMHO there is no realistic scenario where you get the heat production of 4 conductors.
Connecting the 4th wire at the supply end ensures that there is nothing you can do at the load end to get the heat production of 4 conductors at full current (using linear loads), and therefore it becomes only 3 CCCs.
A conductor "capped at one end and energized at the other end" is more like a conductor that is "energized and landed on a bus with no loads connected to it" than it is like a conductor "capped at both ends".
Cheers, Wayne