NRGross
- United States
- Electrical Engineer
Hi All,
I just received a request from a customer that wants 3 sources feeding into one power distribution panel that would then be providing power to equipment inside the room where the panel is located. I am assuming he wants this because he would rather feed power into one place and distribute it throughout the room rather than having separate power drops from outside of the room for each piece of equipment (all sources are located within the same building). I can see this being very tricky using separate disconnects for each source and trying to interlock the disconnects with the door. So, my question is other than labeling that there are more than one power source feeding this enclosure are there any other code requirements for something like this? I had a veteran panel builder say to me to just avoid the headache and option for 3 separate panels rather than one, but from what I can find there are no code violations as long as I am using a separate disconnect for each source and is well labeled stating that this enclosure has more than one source. Please correct me if I'm wrong and please share any tips/experience if you have done something like this in the past.
As an example the power requirements to be in one of the panels are as follows:
480VAC 3p 60A
240VAC 3p 30A
120VAC 1p 30A
Thanks!
-Nathan
480VAC 3p 60A
240VAC 3p 30A
120VAC 1p 30A
Thanks!
-Nathan