Have a customer with a 480/277v service that feeds a 75kva 480D-4160D transformer. The 50 year old transformer has failed, currently running generators to get them going. Customer owned generators, so they don't have too much of an issue running these for a while.
125a 3w w/ ground feed to the transformer location. 4160 transformer feeds 2 outbuildings and pump sheds ~2 miles away. Two of the stepdown transformers are single phase 4160-120/240, connected L-L. Pump shed has a 4160d-480/277wye stepdown. They have a presumably working 75kva 4160/2400wye-480/277wye transformer on hand.
Is this wye-wye transformer useable in this situation? Do I need to provide a neutral to the transformer? RMC 500ft from service to transformer location, so doubtful to be able to get a neutral to it. But is one even needed if there is nothing connected L-N on the 4160 side? I know to leave them floating if you are supplying a wye-delta, but have not run into a wye-wye before. Can have a matching transformer in a week or so, but curious if this will work for now.