Thanks Infinity, I appreciate your input, and the safe-pulling-radius to protect the conductors is logical, and yet, Ts and LBs exist, and the max-conductor allowances are marked in the bodies, for instance 3 - 2/0 in the one I'm looking at, which seems to imply that one could route up to 3 2/0 conductors through, even though the body doesn't come close to the 6X or 8X rule for the 2inch conduit entries.
314.28(A)(3) Smaller Dimensions. Listed boxes or listed conduit bodies of dimensions less than those required in 314.28(A)(1) and (A)(2) shall be permitted for installations of combinations of conductors that are less than the maximum conduit or tubing fill (of conduits or tubing being used) permitted by Table 1 of Chapter 9.
Listed conduit bodies of dimensions less than those required in 314.28(A)(2), and having a radius of the curve to the centerline not less than that indicated in Table 2 of Chapter 9 for one-shot and full-shoe benders, shall be permitted for installations of combinations of conductors permitted by Table 1 of Chapter 9. These conduit bodies shall be marked to show they have been specifically evaluated in accordance with this provision.
Where the permitted combinations of conductors for which the box or conduit body has been listed are less than the maximum conduit or tubing fill permitted by Table 1 of Chapter 9, the box or conduit body shall be permanently marked with the maximum number and maximum size of conductors permitted.
Hard to see how this body or others could meet the Table 2 bend radii, so the markings consistent with the last paragraph seem to imply approval even though it doesn't meet the bend radii. Are conduit bodies like this used for conductors as large as the markings?