C phase on detail burnt up...again

Location
60004
Occupation
Electrician
We are replacing a 1200amp 3phase main breaker again, to the day this was replaced exactly a year ago at a pump station and same issue. The C phase detail connection from breaker to bus, with properly torqued factory replacement carriage bolts melted to nothing. Voltage is 480v, all loads are 3 phase and balanced, we are stumped. The piece fed info from plant employees, was utility company had a surge and blew fuses at there transformer just outside building, and that's when the generator took over. Utility company got us online again, and generator would not shut off, checked line voltages, good, load good, get to ATS further down gear and line side nothing on C phase...cause the buss was blown. Before adding more surge protection, another 1200amp breaker, anyone have any clue on the cause? Like I said, last year after we replaced, all phases balanced and voltages were perfect.
 
The C phase detail connection from breaker to bus, with properly torqued factory replacement carriage bolts melted to nothing.
What was replaced besides the breaker? If anything that was left in place happened to have been overheated to some extent, it could been compromised enough to start the second failure.
 
We are replacing a 1200amp 3phase main breaker again, to the day this was replaced exactly a year ago at a pump station and same issue. The C phase detail connection from breaker to bus, with properly torqued factory replacement carriage bolts melted to nothing.
The only time I ran into that was with old Aluminum Busbar, check that every nut bolt and screw is properly rated for the metal its attached to?
 

Attachments

  • 1750548426564.png
    1750548426564.png
    71.1 KB · Views: 9
What was replaced besides the breaker? If anything that was left in place happened to have been overheated to some extent, it could been compromised enough to start the second failure.
First one a year ago, blew out the back of the breaker behind C phase, old breaker was a Westinghouse NCG, replaced with Eaton/C-H recommended replacement, which came with factory hardware. At the time we just assumed since the breaker ran its life being from 70's. Detail was not changed as it was fine and not effected, during shutdown we torqued all detail to recommendation through out gear.
 