ptonsparky
Tom
- Occupation
- EC - retired
@ $85,000 the owner can afford the proper arrangement for power source.
Is it new? Can you post a link to the saw?. If it wasn't an $85,000 saw
Can you post a picture of the data plate? That would clear up so much confusion.Not entirely certain that it requires a fully balanced system, but certainly it needs 240V phase to phase and 120V phase to ground max.
This definitely helps fill some of the knowledge gap. Is there no delta configuration in 3 phase that gives 120V to ground on all three legs?
Another portion of my knowledge gap... I have a basic understanding of transformers but never have had the opportunity to learn about all the different variations and how it affects the voltages.That is physically impossible.
In a balanced system you either get 208V phase to phase and 120V phase to ground, or you get 240V phase to phase and 139V phase to ground.
My assumption was that it needed to be closer to 120V since they say not to use a high leg. I finally got a sparse schematic from them today and it is originally European (made in Italy), nameplate is 480V, schematics say 400V to motor @50htz. The technician I talked to has some reference material that he did not send me that states "no high leg" and he said a senior engineer told him 245V max for the motor... so I may have another issue as our utilities like to run 245-249VIf this is true, your only choice to use one the previously mentioned wye transformers 240Y/139V (look for a drive isolation transformer) or a 208Y/120V ( a standard transformer but it won't provide 240V).
My guess is that you are not dealing with actual engineering support. The engineering department probably has some suggested method rather than a simple don't do it. The saw is much more than a simply motor, it likely contains several filters for multiple drives and electronics.
The nameplate is incorrect for the machine, they manufacture for 480Y then ship to US and rewire for 240V Delta. Unfortunately they did not swap out tags so I am stuck with the wrong ones. I assumed 120 to ground since they specified no high leg, but must be incorrect.Can you post a picture of the data plate? That would clear up so much confusion.
I’m not understanding why you need all three legs to have 120 to ground either.
I assumed the same but the technician said that it specifically stated no high leg for motor.I would bet the OP's saw is the same way. Just don't put the high leg on the 120V portion of the saw. Other than the 120V portion, the 3ph, 240V portion of the saw would have no idea, or care, that a high leg was being used. All three legs would be 240V line to line.
I've tried a couple times... going to end up costing him more trying to piecemeal it but that is his decision.@ $85,000 the owner can afford the proper arrangement for power source.
That may very well be what it is... It is an FOM USA Panda 550 upcut saw. No documentation or paperwork on their website I could find and very frustrating. Brand new equipmentIs it new? Can you post a link to the saw?
There is a 'universal' equipment design standard for the Americas thats settled on 220Y/127
If its new equipment for the North and South Americas market I'd bet a milkshake its 220Y/127
I have had to correct sales people whom refer to this as the imaginary 240Y120 LOL
Biggest problem is that the high leg is downsized and the service entrance equipment is at least 30 years old. I have tried to convince them two or three times now to just replace the service but I am too nice a guy and like to give people options. The technician did state that the power supply is 220V so it could very well be the case.Equipment labeled 220Y/127 *should* tolerate our 208Y/120 - 240Y/139, even 240 dleta unless it has a VFD internally may not tolerate a open delta as discussed in many old threads.
I would just call and ask your local POCO if there are 3-primaries on the pole to convert the service to 208Y/120.
The Italians do not rewire their machines for American voltages, you have to get them to send the correct auto transformer for the machine voltages. I have several Italian made CNC machines with 240 delta feeding them, and had to make them send a transformer with it.Another portion of my knowledge gap... I have a basic understanding of transformers but never have had the opportunity to learn about all the different variations and how it affects the voltages.
My assumption was that it needed to be closer to 120V since they say not to use a high leg. I finally got a sparse schematic from them today and it is originally European (made in Italy), nameplate is 480V, schematics say 400V to motor @50htz. The technician I talked to has some reference material that he did not send me that states "no high leg" and he said a senior engineer told him 245V max for the motor... so I may have another issue as our utilities like to run 245-249V
Initially that is what I thought a week ago however the machine gets rewired in the US. Power supply gets swapped out, a control module gets replaced, and the motor gets rewired from Wye to Delta, I have talked with the technician who did it on the exact machine I am now trying to power up.The Italians do not rewire their machines for American voltages, you have to get them to send the correct auto transformer for the machine voltages. I have several Italian made CNC machines with 240 delta feeding them, and had to make them send a transformer with it.
Sounds like the Italians are selling the customer a Chinese made machine. My customer has a saw sold to him by the Italians that is made in Hungary, I believe. Took forever to get a wiring diagram out of them, because they didn’t make the machine, they only put their name on it.That may very well be what it is... It is an FOM USA Panda 550 upcut saw. No documentation or paperwork on their website I could find and very frustrating. Brand new equipment
Is this VFD driven motor or across the line manual/magnetic contactor controlled? As many already mentioned the motor won't care about high leg or even corner grounded systems. VFD's however may not be designed for anything but 120 nominal to ground on all three lines. On board single phase controls?control transformers simply need be connected to the non derived phase if on a rotary converter as that voltage isn't always a stable 240.Unfortunately the tech support does not know the answer either other than "the specs say not to use a high leg." The machine costs $85,000 so I have zero interest in experimenting to find out why
Thanks for the welcome. Seems as though Delta-Wye will be the best solution as I cannot seem to convince them to replace there service
Thank you sir, I will take a look
I agree, but waiting on the manufacturer for more information currently. Pole has 2 pots, if memory serves correctly, the high leg comes off its own pot and the two normal phases are off the second one. Service is 400A fused disconnect. High leg is 210V to groundSeems to me that conversion to 480 V wye, @ 60Hz would have been the most practical choice.
The motor will run fine at that. What needs to be done with the control power is unknown.
That's a standard voltage transformer output here. What is unknown is if the site has an open delta service or not.
That could be an issue with voltage stability, depending on service size and other loads connected to the same service transformer bank.
Do you know if the service is supplied open delta ( two transformer pots instead of three) and what size is the service that they have existing ?
Schematics show thermal magnetic contactor, however I believe there is a power supply between the contactor and motor that converts to 220V. I am beginning to think perhaps the power supply is what cannot handle the high leg.Is this VFD driven motor or across the line manual/magnetic contactor controlled? As many already mentioned the motor won't care about high leg or even corner grounded systems. VFD's however may not be designed for anything but 120 nominal to ground on all three lines. On board single phase controls?control transformers simply need be connected to the non derived phase if on a rotary converter as that voltage isn't always a stable 240.
Thanks for the more in depth explanation. This converter had 267V phase to ground, significantly higher than the incoming from utility...Back to the concept of the rotary phase converter
They specified 240V for the machine and it was rewired from 480Y to 240D but apparently cannot have a high leg which makes no sense to me. Once again I am thinking the power supply may have something to do with it. I am waiting on the manufacturer to send the paperwork that specifies it. It may also be an artifact of the 480Y system that made its way into the 240D system since they seem to copy and paste a lot...If it is a new machine and ordered for where it is being installed, the question might be why did it not get ordered for what the existing supply has, or at least with conversion equipment to work with what is there? 240 volt high leg delta is not that rare of a system in North America. Some areas maybe is more rare than others but you can find these almost everywhere in the US to some extent.
Two pots is an open delta service. One phase from the larger of the two pots, (two lines L1 & L2), with a center taped coil with the neutral tapped in the middle of that pot coil.Pole has 2 pots, if memory serves correctly, the high leg comes off its own pot and the two normalphaseslines are off the second one. Service is 400A fused disconnect. High leg is 210V to ground
Yeah thats what I'd quote along with getting a quote from the POCO to either close the delta or if they are a POCO thats getting rid of delta's I might even ask them for a cost esitmate on providing a 220Y/127 service at the customers expense as neither of those involve any changes on the customer side.but I would recommend the 240Y/139 as it gives you the chance to have a grounded secondary.
I doubt that, the EU's Low Voltage Directive (LVD) (2014/35/EU) state for their nominal 230V supply, the permitted voltage variation is +10% and -6%. This means any equipment made for the common market should accept a voltage range from 207V - 253V.and he said a senior engineer told him 245V max for the motor... so I may have another issue as our utilities like to run 245-249V