I don't either. Based on the average high ambient temperatures in my area the trip for one brand of breaker will be at least 25% above the handle rating for about 5 months of the year.I don't like the idea of a main breaker outside in the elements,
I am thinking about a PI that will require the interior panel to also have a main breaker with a rating not exceeding the ampacity of the feeder conductors. The outside breaker would provide the short circuit and ground fault protection for the feeder, and the interior one would provide overload protection for the feeder and the panelboard.