Ashu
- Hunt Valley, USA
- Electrical Engineer
Good morning, everyone,
NEC doesn't seem to have any code specifying how to calculate an isolation transformer (same primary and secondary) size. In my case I need to find an optimized way to size the isolation transformer which supplies to a machine having hundreds of motors. Most of the motors in the system are Servo motors which are sized for the peak load requirement; however, the actual draw is very less. In some cases, it is only 25% of the rated nameplate data.
Historically, we have considered the sum of actual motor nameplate data plus 15% additional for the isolation transformer calculation. However, actual machine current draw is much less than that.
The question I have is should I be allowed to use the actual current draw of the machine (with some safety factor) and not based on the rated motor currents?
If yes, I see a possible indirect issue: I would assume, the side effect of it will be a reduced sized cables and breaker from the plant side which supply to this transformer. Similarly, reduced sized cable supplying to the machine. However, machine's main circuit breaker is calculated based on article 670.4 which states that the supply conductors will have ampacity not less than 125% of the highest rated motor plus the sum of other loads. This means the machine's main breaker will be larger than the plant circuit breaker supplying to machine through isolation transformer.
I am stuck in this loop while trying to optimize the transformer size to save huge cost for the machine. I will appreciate any guidance on this.
Thanks.
Thanks.