The reason so many think ground = safe is all emphasis put on "grounding" things. You can't splice a grounding electrode conductor. Specs still call out for ground rods for street lights. Highly paid engineers want you to drive ground rods in the shape of a triangle. The NEC tells us you have to try and drive a ground rod straight down and see if something stops it before you can drive it at an angle. I see ground rods installed at the stupidest places like a 500V DC EV fast charger.The word grounding in the existing term is the reason many think you can just connect it to earth and it will be safe.
Yeah, but the ground or earth is probably the least consequential component in the entire system. "Ground-fault" itself is a term that is rarely the case. It is usually a grounded conductor fault and ultimately, even when the fault is to the earth its final destination is the grounded conductor.Grounding Conductor, Equipment (EGC). - A conductor path(s) that is part of an effective ground-fault current path and connects normally non-current carrying metal part of equipment together and to the system grounded conductor, or to the grounding electrode conductor, or both.
it's more than just a wire bonding conductor. it's the entire equipotential bonded system, including conduits and other metal framework.
An Equipment Grounding Conductor is for clearing a fault. A bonding conductor could be for anythin
Not 100% correctAn Equipment Grounding Conductor is for clearing a fault. A bonding conductor could be for anything.
In ground pools require bonding conductors that are not required to be EGC. Cell sites have gobs and gobs of bonding conductors on every piece of metal equipment on the site. FAA requires an extra bonding conductors on the outside of every run of flexible conduit. While all of them may wind up as part of a fault clearing path none of them are part of the NEC requirements for Equipment Grounding Conductors.Not 100% correct
Thats pretty good I like that one.FCC
Fault Clearing Conductor
The least important conductor in the whole electrical system has the most restrictive rules about splices.GECs may be spliced in certain conditions and by specific means.
you mean the least-appreciated conductor. feel free to disocnnect your house from the earth, and you'll quickly learn it's importance.The least important conductor in the whole electrical system has the most restrictive rules about splices.
Change one term in the code and all the myths, misunderstandings, and electrical injuries go away. It's easy. You can't see that? I mean it makes so much sense.It is puzzling why the NFPA (CMP's, whatever) are so steadfast in their reluctance to correct the grossly incorrect grounding stuff in the code. Changing EGC to EBC might help with grounding myths but there is s while bunch of other stuff that needs to change too.
No. I mean the least important. There are houses lacking earth connections everywhere and no one is aware of it. Life is not impacted in any way.you mean the least-appreciated conductor. feel free to disocnnect your house from the earth, and you'll quickly learn it's importance.
be sure to go out and disconnect the ground rod connection from your transformer as well.
what do you think will happen? Connection to earth is not really important for the safety of the electrical system.you mean the least-appreciated conductor. feel free to disocnnect your house from the earth, and you'll quickly learn it's importance.
There was intense discussion on replacing EGC with EBC, but once that discussion was finished, they did not want to revisit it again...in fact one of the negative voters on my proposal came back the next cycle and said he changed his mind, but the rest of the panel said that ship had already sailed. If he would have voted for my proposal, that would have given panel 5 the 2/3s majority needed to make the change.It is puzzling why the NFPA (CMP's, whatever) are so steadfast in their reluctance to correct the grossly incorrect grounding stuff in the code. Changing EGC to EBC might help with grounding myths but there is s while bunch of other stuff that needs to change too.