jim dungar said:
The system is correctly called a 240/120V 3-phase 4-wire delta.
Slang terms for this type of system include: Wild Leg, High leg, Christmas Tree, and Red leg.
208V loads are not encouraged.
There are usually no single pole 208V rated breakers available for the common panels found on these 240/120V systems. The transformer bank that creates this system has usually not been sized for the unbalanced effects a 208V load would create.
often, what's up on the pole is 2 transformers in an open delta configuration,
not really designed for a single phase 208 volt load.
as far out on the edge as i've ever seen done is some old WW2 machine
tools that were 240 volt delta with across the line 240 control voltages
and they had to be rewired to run on 480.
the motors could be rewired without problems, they were 12 lead motors,
and the contactors were obviously fine, but the
polish and german contactors had coils that were unobtainable
anywhere, and were 240 volt. however, they were built like tanks,
and meggered well, and have been running for about 19 years on the
277 volt leg to ground of the 480 system without problems. no motor
burnups either. stuff built back then was built pretty sturdy. the only
shortfall was the heaters. correctly sized ones were not available,
so running overcurrent protection is virtually nonexistant.
it isn't something i would do, from a liability standpoint, but it has
stood the test of time.
randy