240v UPS
MBLES
i have a customer who wants to back up power using a UPS system for a few hours without using a generator. They would need 125a 240v 1 phase. i have only seen and installed UPS or power bay with 24v rectifiers with 240v power supply. i have been asked to install a 240 dc to 240v ac. Any thoughts on a system that can do that??
Liebert or APC might have something but you'll run into two gotchas- most UPS that size are 3-phase and that's a really long run time; 30Kva/hour is a lot of batteries for that size UPS. If nothing else that's a fair amount physical space and you need to make sure the charger is up to charging that big a stack while also supplying the load.
You might be better off breaking the load across two or three individual UPSs.
Why no generator?
A LOT of batteries...
Non-electrical people often have no way to conceptualize what it means to say "125A for a few hours". Just to give you an idea, a Liebert 30kVA UPS with internal batteries is maybe 15 minutes of hold-up time. To get 2 hours, you would likely need their largest external battery rack. The UPS with the internal batteries is 24W x 40D x 79H and weighs 678 lbs, an external battery unit that MIGHT be capable of 2 hours of backup is another cabinet, 35W x 40D x 79H and another 1678 lbs! So you are looking at well over a ton of equipment here...
And as noted, this is 3 phase only.
Oh, and you are looking at somewhere in the neighborhood of $50,000